[SML] Dimming Cooling
Paul Marsland
pmarsland at gmail.com
Thu Aug 27 14:28:41 UTC 2015
Take max dimmer capacity (mdC)
derate to 80%
dimmer manufacturer will tell you efficiency (97% for ETC Sensors), so
3% is lost to heat (EtoH)
so = watts lost to heat (wl2H)
convert wl2H to BTU
mdC * 80% * 3% * 3.412 = BTU/hr
And install a thermostat. :) We have dimmer rooms with and without,
for some reason...
Paul Marsland
+1 (919) 239-0551
On Thu, Aug 27, 2015 at 10:14 AM, Stephen Litterst via Stagecraft
<stagecraft at theatrical.net> wrote:
> Question for the consultants and dimming specialists out there. What BTU
> figure do you use for dimming racks to calculate the HVAC needs for the
> room?
>
> The AC in my dimmer room died and I want to make sure to pass along the
> right number to the HVAC folks for replacing it. (And for myself to get
> something in there to limp along until the replacement is done.)
>
> Thanks!
>
> Steve L.
> --