Just a comment on the auto-taps. I'm sure your electricians know about
it, but just in case it's worth noting. When you get a brownout and the
transformer switches, your Amp draw will go UP by about the same
percentage as the brownout goes DOWN. Not a problem unless you're
running close to full capacity and you have a deep brownout.
On 01/15/2015 06:37 PM, Michael Sauder via Stagecraft wrote:
>
> The wildcard is that we don't know how much of a problem any of this
> really will be. The recommendation I just made to the producers is to
> install an automatic tap transformer to start (we need a step-down
> transformer anyway, this is just a fancier version), a quality power
> monitoring solution so we can gather data and tie into the show
> controller (Medialon Manager), and designate infrastructure space
> where we can put in a $$$ power conditioning system in the future, if
> needed.
>
> Thanks again to everyone for their help, it has been extremely helpful.
>
> Michael S.
--