<div dir="ltr"><div>We had a much older panel, but it was recently upgrade when they added onto the building.  I've worked out how to do it with the fire alarm company, my OP was more in-line with how to get such a bypass approved by the fire marshal.  He's willing but wants to make sure he covers things on his end as well.</div><div><br></div><div>-Jonathan<br></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Tue, Oct 3, 2023 at 2:45 PM Riter, Andrew <<a href="mailto:andrew.riter@ubc.ca">andrew.riter@ubc.ca</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><div class="msg6934201420711057939">





<div lang="EN-US">
<div class="m_6934201420711057939WordSection1">
<p class="MsoNormal">Hi Jonanthan<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">(writing from Canada, with a 26 year old system, YMMV)<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">In our scenarios, there isn’t a “switch on a wall.”  The Fire Life Safety electrician for the university comes over (“Fire Watch”), and on the main panel bypasses certain activation systems (smoke detectors).<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">I expect any main control panel can do this, depending on the age and technological level of the main panel.<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Is that your type of panel, or do you have something simpler (and not adaptable?)<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Good luck<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Andrew M. Riter<u></u><u></u></p>
<p class="MsoNormal">Chan Centre<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">604-808-2033 (working from home)<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><b>From:</b> Stagecraft <<a href="mailto:stagecraft-bounces@theatrical.net" target="_blank">stagecraft-bounces@theatrical.net</a>> <b>
On Behalf Of </b>Jonathan Zitelman via Stagecraft<br>
<b>Sent:</b> Tuesday, October 3, 2023 5:51 AM<br>
<b>To:</b> Stagecraft <<a href="mailto:stagecraft@theatrical.net" target="_blank">stagecraft@theatrical.net</a>><br>
<b>Cc:</b> Jonathan Zitelman <<a href="mailto:jzstagecraft@gmail.com" target="_blank">jzstagecraft@gmail.com</a>><br>
<b>Subject:</b> [SML] Fire Alarm Impairment<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<table border="0" cellspacing="0" cellpadding="0" style="border-collapse:collapse">
<tbody>
<tr>
<td style="padding:0.75pt 0.75pt 0.75pt 0in">
<p class="MsoNormal"><span style="font-size:9pt;font-family:"Arial",sans-serif;color:black;background:rgb(255,236,179)">[<strong><span style="font-family:"Arial",sans-serif">CAUTION:</span></strong> Non-UBC Email]</span><u></u><u></u></p>
</td>
</tr>
</tbody>
</table>
<div>
<div>
<p class="MsoNormal"><span style="font-size:10pt">Poking out of my dusty little corner as I do every several years.<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10pt"><u></u> <u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10pt">I know many theatres and hotels have a switch which has been programmed into the fire alarm system to disable specific initiating devices within the fire alarm system.  Typically these are smoke detectors
 associated with fog/haze use, located directly around the stage.  Actual use of the switch usually requires a permit and fire watch or fire inspector on site to still meet Life Safety Code, and the full system is not taken off-line so that patrons are still
 alerted if necessary.<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10pt"><u></u> <u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10pt">I have reached out to our fire marshal about installing such a switch.  He's amicable but has asked what reference allows for this exception.  I've tried searching online and have found a few universities
 with guidelines and applications (and learned a lot about fats, oil and grease [FOG]), but cannot locate any specific references other than a blanket reference to NFPZ 72: National Fire Alarm and Signaling Code.  At over 400 pages and the inability to search
 while using free access, I was hoping someone here might be able to provide some more specifics.<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10pt"><u></u> <u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10pt">I know this has to be done correctly as it directly involves life safety.  Despite our best efforts to date, we still end up with one or two false alarms a year.  Again, I appreciaite any insights, until then
 I will be leafing through code in my spare time.<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10pt"><u></u> <u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10pt">Thanks!<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10pt">Jonathan Zitelman<u></u><u></u></span></p>